Propane supply line extension.
Propane in basement? from what I was told, no propane applinces(sp) in lower level unless vented shall be installed..
I've done new installations of Naturel Gas, but never worked with the "heavier than air gas". I'm nervous about extending the supply line from an existing furnace to a newly installed tankless water heater. The new unit is ready to go except for the fuel line. I don't want to blow up the house, not to mention myself. The basement has glass blocks in the windows, with only a 4"*10" hopper type opening. In other words the basement dosn't have very good ventilation. There isn't a shut off valve that I can work back to. There are two regulators, but I won't be able to exhaust the line between the secondary regulator and the basement. Is disconecting the primary line at the tank going to be good enough? Is anyone willing to venture a guess? I know the orriginal supply line may be too small to supply the furnace and the new tankless heater, but sizing is a seperate issue.0 -
You cannot disconnect the piping for venting because of the regulators. Can you disconnect the piping at the tank, and fill the pipe w/nitrogen or other inert gas? Would this dilute the gas past the regulators? I do not remember the UEL and LEL for propane, but surely the amount of gas in the piping should be so small the explosion possibility should be minor. Of course "minor" could be considered a relative term if you are in the middle of a "minor" explosion. Have you contacted the propane supplier for suggestions?
fireguy0 -
gas cocks and unions
are supposed to be just outside at the service entrance and within close proximity (but outside of) each and every appliance. If they are not, you should make the upgrade. LP gas appliances installed in a basement or pit where heavier than air gas may accumulate are conspicuosly not mentioned in the International Code; but a battery backed up gas sniffer/solenoid is usually acceptable (but not in all areas). You may have "a can of worms"; please be careful.0 -
careful
Propane is common here. There should have been a valve after the secondary regulator.
If not , just shut it off at the tank.
Watch your pipe sizes, especially for a tankless.
I bet it's too small, you may have to re-pipe everything.
CSST and manifold may be way to go, for all appliances.
Pressure and leak test all connections, as you would NG.
If you feel uneasy, then just contact gas supplier, they'll send someone out
to re-pipe inside house also, unlike a NG utlity company.
You might have to be certified
to work on LP in your state or area. We have a state wide certification for all installers and delivery personal.
Generally the company that supplies or leases the tank has licensed "fitters" on staff.
If LP makes you nervous, sub that part of the job to someone with the experience, code knowledge,and adequate libility insurance to cover LP work!
Better safe than sorry.
hot rod
- 86.7K THE MAIN WALL
- 104 Chimneys & Flues
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 939 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 43 Industry Classes
