Warm air comfort

Brad White_9
Member Posts: 2,440
is 130 degree supply water but like any rule there are exceptions/circumstances.
The general concern which I am sure you know is that the space tends to be dryer in winter hence more skin evaporation, hence the actual supply air temperature has to be warmer to compensate. IOW: If you humidify you can get away with cooler supply air temperatures than if you do not.
What you have going for you is using what is normally a cooling coil: More rows typically, therefore a given water temperature will perform better than in a coil with fewer rows.
As a footnote, watch your leaving water temperature (return water to the boiler) should it not be of a condensing type. Multiple row coils can sub-cool that water in a hurry, to below dewpoint. If you have a condensing boiler, go for it.
The advice you got on trying it and adjusting it is the best way to go, all things said. You might get a table from the coil manufacturer, but in the end, you are going to play with valves anyway, aren't you? :)
The general concern which I am sure you know is that the space tends to be dryer in winter hence more skin evaporation, hence the actual supply air temperature has to be warmer to compensate. IOW: If you humidify you can get away with cooler supply air temperatures than if you do not.
What you have going for you is using what is normally a cooling coil: More rows typically, therefore a given water temperature will perform better than in a coil with fewer rows.
As a footnote, watch your leaving water temperature (return water to the boiler) should it not be of a condensing type. Multiple row coils can sub-cool that water in a hurry, to below dewpoint. If you have a condensing boiler, go for it.
The advice you got on trying it and adjusting it is the best way to go, all things said. You might get a table from the coil manufacturer, but in the end, you are going to play with valves anyway, aren't you? :)
0
Comments
-
Quick heat and comfort
I have a project where I am supply heat(hot water) to a fan coil unit. The primary use of the unit is for cooling. This is a 2nd home and will be turned down when it is unoccupied(60 degres). The owner would like a quick heat source to bring the home up to temp. So I am supply heat to the fan coil. What my question is how low of supply temps can I provide to the fan coil and not lose comfort-blowing cool air. I am installing a condensing boiler so I would to keep the supply temps as low as possible, I spoke with the HVAC contractor and he said the unit needs 140 to operate BUT can be adjusted lower if needed. I am just concerned about comfort.
Thanks Jeffrey0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 939 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements