Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Diverter-Tee Hot Water Heating

DanHolohan
DanHolohan Member, Moderator, Administrator Posts: 16,600
2" behind and 3" above. Be aware that this will cut 20% off the radiator's rating, though. Use reflective insulation behind the radiator. The second radiator's diverter tees can be as close as you'd like.
Retired and loving it.

Comments

  • Jack_34
    Jack_34 Member Posts: 2
    Diverter-Tee Hot-Water Heating

    I have 5" deep radiators - how much clearance top back and sides when recessed in interior wall? Also, what type of backing between back of rediator and back of sheetrock wall? Also, in same wall but next room how close can I put the diverter tees after diverter tees for radiator in previous room?
This discussion has been closed.