Vitodens Temp Display
Brad White_75
Member Posts: 15
from Harald Prall no less. How can you top this place?
0
Comments
-
Comfortrol Display
Hey Guys,
Who knows the coding address to switch a Vitodens Comfortrol from displaying Celsius to Farenheit?
Thanks,
J
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Vitodens Temp Disply
Comfortrol must be in boiler, open lid , system D , installer set up C , code BCCB , coding level 2 , B button-
press backwards - goes faster , adress OD6 , value 000 = Centigrade - value 001 = Fahrenheit , press D to transfer,
close lid , I hope this is of assistance.
Harald0 -
???
It's right in the manual for service and troubleshooting. If you haven't taken the time to read through it and code the control to match your system, C/F will be the least of your worries. Read it man, read it! OD6 is correct.0 -
Hey C'mon ease up.
At least i know what a Vitodens coding address IS!
I do indeed go through the literature, just didn't see that one this time through.
Have a great weekend.
J
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
walking among the demigods...
... the wall is a great place...0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements