Oil Burner
Reed
Member Posts: 56
Ed NYC. You say to run one pipe out of top of tank to burner, ( which is not a problem). My question is still will the pump on the burner (Beckett AFG) be able to pull the oil approx. 60'? The length includes coming out of the tank, across the basement ceiling and down to the burner. Thanx.
0
Comments
-
Oil burner is far from oil tank
Thank you for all the responses to this message. (had posted it about a week ago). Learned about a tiger loop. Had never heard of this before. I'm new to this site and am allways learning something. There's alot of knowledge here and I appreciate it.0 -
CRP&H
Yes it should be no problem pulling 60' overhead and down again once the oil is over the top and down the burner side syphon effect will cancel out the rise. Just use the Tigerloop chart to determine line size.0 -
tigerloops
these babies are great and are recommended for all installs. you'll notice on the annual service how clean it's possible to run a oil system
They call me "Hot Pipe"0 -
I agree with Bruce
You can try running the overhead line and connect it right to the burner without a Tigerloop and take a vacuum reading to see if it is in specs . If it's running a high vacuum , add the Tigerloop . We recently ran about 50 feet of overhead oil line to a Riello . After priming the burner ran fine , without the de-aerator .
I'm not against using Tigerloops , but I've seen them spew oil in the form of bubbles out the top . I use them only when necessary .0 -
spew?
was that the old loop or the redesign?
They call me "Hot Pipe"0 -
The old one
I think ? We use a different brand now with 2 floats . I forget the name but I think it's German with blue floats . Still , I've seen oil bubbles come out of this one also . On startup , but it happens .0 -
Ron,It's an Afriso.I've used them with no problems
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
That's it
The job where we had some bubbles come out had a pretty high lift and the oil line was empty . After priming we turned the boiler off to let the bubbles settle and it worked fine after .0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements