Approach Temperature
Eugene Silberstein 3
Member Posts: 1,380
When you calculate subcooling, you measure the liquid line temperature and then substract it from the condenser saturation temperature to obtain subcooling, right?
Well, when you use the approach temperature method, you are charging with respect to outside ambient temperature and liquid line temperature.
Check this out:
Let's say you are dealing with a standard efficeincy system and you are using the 30-degree rule of thumb as the difference between condenser saturation temperature and the outside ambient. For example, if the outside ambient temperature is 85 degrees, the refrigerant should be condensing at a temperature of about 115 degrees. Now, let's say you want 25 degrees of subcooling. The liquid line temperature should be about 90 degrees.
The difference between the outside ambient (85 degrees) and the liquid line temperature (90 degrees) is 5 degrees. THe "approach" temperature is therefore 5 degrees.
Lennox is basically eliminating the calculations for you.
For a higher efficiency unit, the delta-t between the outdoor ambient and the condenser saturation temperature may be 25 degrees and the system may be operating with 21 degrees of subcooling. In this case the approach temperature would be 4 degrees.
Cool, huh?
Well, when you use the approach temperature method, you are charging with respect to outside ambient temperature and liquid line temperature.
Check this out:
Let's say you are dealing with a standard efficeincy system and you are using the 30-degree rule of thumb as the difference between condenser saturation temperature and the outside ambient. For example, if the outside ambient temperature is 85 degrees, the refrigerant should be condensing at a temperature of about 115 degrees. Now, let's say you want 25 degrees of subcooling. The liquid line temperature should be about 90 degrees.
The difference between the outside ambient (85 degrees) and the liquid line temperature (90 degrees) is 5 degrees. THe "approach" temperature is therefore 5 degrees.
Lennox is basically eliminating the calculations for you.
For a higher efficiency unit, the delta-t between the outdoor ambient and the condenser saturation temperature may be 25 degrees and the system may be operating with 21 degrees of subcooling. In this case the approach temperature would be 4 degrees.
Cool, huh?
1
Comments
-
I'm just curious.....
...as to why some manufacturers (Lennox comes to mind) tell you to check your charge using approach temperature rather than subcooling.
Just worked on a unit yesterday where we had to relocate the condenser due to an addition being put on the house. It's a Lennox 2.5 ton unit with txv at the evaporator coil.
Lennox specifies a 5 degree +/ 1 approach temperature. I was able to achieve it, but why not use subcooling?
Starch0 -
Thanks, Prof!
I figured there was a connection there somehow, but couldn't see it in my mind's eye!
Thanks for the explanation!!!
Starch0 -
No problem!
Always a pleasure to help.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements