Munchkin
Shaun Anderson
Member Posts: 164
Can you flip the cover off a V-1000 to have exhaust on top rather than bottom ? In my installation manual it shows exhaust on bottom but doesn't say that its a must. Any problems or concerns ?
TheFuture
TheFuture
0
Comments
-
I would rather
see the exhaust on the top.When the unit is in low fire with just a slight breeze, you may pull exhaust gas in with the fresh air. I recomend, always putting the exhaust above the fresh air intake, with any gas appliance.
I hope this helps,
If you have any questions, please feel free to call us tommrow durring normal buisness hours.
Chuck Shaw
Technical Support Department
Heat Transfer Products0 -
This is what me and my contractor wanted to hear. Can't keep enough Munchkins on the shelf. Love'em