Munchkin Madness

Rick Kelly_3
Rick Kelly_3 Member Posts: 47
Just wanted to share some pics of our latest Munchkin install. Another "closet" job.

Comments

  • S Davis
    S Davis Member Posts: 491
    Backflow


    Rick,

    Not trying to be a smart **** but I don't see a backflow preventer, are they not required where you are?
    Nice clean jod by the way.

    S Davis

    Apex Radiant Heating
  • Chuck Shaw_4
    Chuck Shaw_4 Member Posts: 66
    Also,

    I noticed you changed the fitting on the end of the condesate drain. Did you drill a hole in the top of the fitting you used for to vent the drain? If not, you may have condensate back up issues.

    Nice looking job.

    Chuck Shaw
  • Wayco Wayne_2
    Wayco Wayne_2 Member Posts: 2,479
    Oh my God!

    you painted the flu and air intake pipe. Looks great. Where will it end, this "Munchkin Madness." :P WW

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Steve Ebels_3
    Steve Ebels_3 Member Posts: 1,291
    Chuck

    Say that again. I'm not following what the deal is with the condensate drain.
  • Chuck Shaw_4
    Chuck Shaw_4 Member Posts: 66
    Steve,

    The factory installed fitting is a straight "barb to barb" connector. It has a small hole drilled into the top, to vent the condensate line, and help it to drain freely.

    In the photos, I noticed that the condesate fitting had been changed, and I wanted to make sure that he had some way to allow air, into the discharge side of the condensate drain (after the trap) for good flow and drainage.

    Chuck
  • Steve Ebels_3
    Steve Ebels_3 Member Posts: 1,291
    I see

    Said the blind man.

    Thanks Chuck
  • Harold
    Harold Member Posts: 249
    Drain

    I am trying to understand what I am looking at (homeowner). If the drain is where I think it is, isn't it going up hill? Shouldn't it keep a downward slope to keep condensate from accumulating in the drain pipe. The way it looks, the bottom of the 90 degree elbow going into the white PVC is higher than the bottom of the boiler but I don't know what it looks like inside and where the real botom of the heat exchanger is, so this may be untrue. It would seem possible that the little hole referenced would leak condensate as installed. Or have I just misunderstood the whole thing?
  • Chuck Shaw_4
    Chuck Shaw_4 Member Posts: 66
    Harold,

    I understand exactly what you are asking, and seeing. I am not a photography expert, but I believe the camrera angle may be somewhat to blame.

    You need to maintain a certian amout of fluid in the drain to keep exhaust gas from pushing through. The level of the heat exchanger is about 1/2 inch, above the discharge of the condensate drain.

    Hope this helps,

    Chuck Shaw
  • Rick Kelly_3
    Rick Kelly_3 Member Posts: 47
    drain issues

    Yes, there is a 7/16" hole drilled into the horizontal branch of the drain tee. The backflow preventer is upstream for lack of room on the main board. The drain does indeed pitch downhill. There's a certain amount of distortion when one is squished into a closet to take pictures.