Pipe Sizing
Options
Brad White_103
Member Posts: 14
You got it, Todd-
If you have a given flow rate the only variable you can work with is the temperature drop.
Take your 50 GPM for example. Yes, you can get 500 MBH out of it at a 20 degreee delta-T, but a million if a 40 degree delta-T, two-million if an 80-degree delta-T.
The best use of high delta-T's is with injection systems where the secondary circuit has much lower temperatures. A little 180 F. water can make a lot of 100 F water for a radiant floor as one example.
The effect of course is diminished when you need higher average water temperatures such as a fan coil system.
You got it.
If you have a given flow rate the only variable you can work with is the temperature drop.
Take your 50 GPM for example. Yes, you can get 500 MBH out of it at a 20 degreee delta-T, but a million if a 40 degree delta-T, two-million if an 80-degree delta-T.
The best use of high delta-T's is with injection systems where the secondary circuit has much lower temperatures. A little 180 F. water can make a lot of 100 F water for a radiant floor as one example.
The effect of course is diminished when you need higher average water temperatures such as a fan coil system.
You got it.
0
Comments
-
Pipe Size for HW Boilers
I am trying to confirm the max BTU's I can flow through a black pipe. What we have is a fhw system with several 2" black drops from a 6" main. According to "pumping away" we can flow 50gpm through 2"iron pipe. If we need to get more BTUs through the 2" drops is that simply a function of a differant delta T??? or is 50gpm good for 500mbh and that's it??0 -
Thanks Brad
0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements