steam header
Options
captbuderus
Member Posts: 10
I have a V85 Steam boiler to pipe. I can get by with a 2" header. Other than a little more cost, I would like to increase it 1 size to 2 1/2. Good idea or no?
0
Comments
-
Definitely
increase the size of the boiler main if you can . I believe one 2 inch riser is the minimum up to the V86 . Although it isn't required , Burnham recommends using both 2 inch tappings on the boiler . With a steamer that size I would recommend using the 2nd tapping also . Please take some pics Cap'n . It's been a while since I've installed a steamer ........0 -
The bigger steam chamber will add to the drying of the steam, if your going with the two risers like ron said (and he's right on the money ) do a drop header it make the conections so much easyer,
hey ronjr we doin a steamer this year for oil heat cares??? realy looking forward to it!just buffed up the old pipe wrenches LOL...David
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements