steam heat
Robert O'Connor_12
Member Posts: 728
Site unseen it sure sounds like a venting problem. When you say "The valves were all changed last year" it sounds as if you may have threw off the balance of the system. What was the reason for changing these vents in the first place? Were you losing water in the system and saw that they were leaking? Other vents located on the mains in the basement are also potential culprits. Without enough (or the right size) main vents can also be problematic. Have you noticed alot of banging? Whats the boilers pressure-trol set at? Got any information or pictures of the boiler?
Robert O'Connor/NJ
Robert O'Connor/NJ
0
Comments
-
steam heat
We have problems with our steam heat in a 15 unit apartment building. The timer and gas boiler are located in the basement. Several people are too hot and I am usually too cold. More of the people are colder in the front of the building, but everyone in the back is too warm. The valves were all changed last year-( larger openning for more heat, smaller for less heat). Some have suggested I get new windows and more carpeting. But I think there is a bigger problem. What should we be looking at to resolve this problem.0 -
what type of control ?
what type of control are you using to run the heating system? where is the building located?how many stories is the building?0 -
steam heat reply
There is a timer in the basement, and a sensor heat timer under the stairs outside,. Building is in Brooklyn, NY and is 4 stories.0 -
steam heat reply
They thought that the hot apartments would get less heat if the valve was set with smaller outlet, and the colder apartments would get more heat with a larger outlet vent. There have been some radiators that leak, and we ususally have to call a plumber to fix the leak. There has been some banging noises in some radiators, and some hissing noises. I'd have to find out more about the boiler pressure. Occasionally there are some loud noises coming from the boiler room too, but it may be the hot water heater considering it makes noise during the summer too..0 -
Main
> They thought that the hot apartments would get
> less heat if the valve was set with smaller
> outlet, and the colder apartments would get more
> heat with a larger outlet vent. There have been
> some radiators that leak, and we ususally have to
> call a plumber to fix the leak. There has been
> some banging noises in some radiators, and some
> hissing noises. I'd have to find out more about
> the boiler pressure. Occasionally there are some
> loud noises coming from the boiler room too, but
> it may be the hot water heater considering it
> makes noise during the summer too..
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Main Vents
sound like the problem here. You have to vent all the air from the mains quickly before steam starts rising to the radiators. I'll bet the hotter units are the ones closer to the boiler, while the ones further from the boiler are cold.
Many old systems did not have main vents. When boilers ran on coal you could get away with this, since the steam was up all day. Once the air was out, it stayed out- so what if it took an hour or two to get heat to the ends of the system? Nowadays we don't have that kind of time.
There are many good steam men in the NYC area, but I'd suggest you talk to Matt "Mad Dog" Sweeney of Triple Crown P&H in Floral Park. He put a brand-new steam system in his own house and it works perfectly. So I know he can make your system work properly. Go to the Find a Professional page of this site, type in your zipcode and follow the instructions to locate his information.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
picture attached, also pressuretrol at top.0 -
picture attached0 -
picture attached0 -
balancing problem
what say the boss at vigilante plumbing ? he should be more than cabable of correcting the problem if possible. they have always been a reputable & knowledgable firm. coupled with the advice gotten here maybe you could give him a shot at it. doesn't seem like a major problem but steam can be a little tricky to balance.0 -
Mary Ann,
My company has been servicing Brooklyn and Manhattan since 1976. We are skilled steam system troubleshooters, I assure you, and I'm certain we can work together toward a solution to your problems. Please feel free to contact me at your leisure.
John A. Cataneo, Jr.
Gateway Plumbing and Heating
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements