more bad kitec

Brian
Member Posts: 285
Where's the job located and what sort of water conditions do they have there?
Dobber
Dobber
0
Comments
-
split kitec
Took this out of a crawl space friday night.Dark spot on aluminum is a hole. Note bumps on pipe and discolotation.
3/4" dhw about 140 degrees with recirc. We still have to show it to kitec.0 -
something else
I just noticed this. Now that the pipe is at room temp, the inner layer has shrunk. Both ends look the same.0 -
Rich,
Give me a call. We will be happy to help you out. Our direct line is 1-800-473-9808
Thanks0 -
kitec problem
Hmmm. Inner liner has no oxygen barrier. Chlorinated hot water being circulated. Chlorine a potent oxidizer. Chlorine meets aluminum. Pretty predictable result.
The big difference between US water systems and European water systems where pex plumbing was developed is the use of chlorine in US systems. Belatedly producers of pex have been trying to address the chlorine issue. About all they can do is adjust the anti-oxidant package: Which helps: but I am not persuaded they can make it good enough to withstand the constant exposure of a recirc line.
When you get to Pex-Al-Pex, the issue gets dicier. The pex layer interior to the aluminum layer is quite thin. Not much room to pack in a large anti-oxidant package. Therefore, I expect pex-al-pex will fail rather quickly in a chlorinated hot water recic line and I don't think there's much the manufacturer can do about it.
Bill0 -
Kitec carries the NSF P171 CL/R continuous recirculation rating, the most stringent chlorine rating in the industry.0 -
split
Please forgive my limited knowledge on plastic tubing in general, but that type of failure would yell pressure to me: What type of expansion protection is on the system? I would think that a hotel would have rush HW times, then recovery time. A large HW maker with a high recovery demand and capability and limited expansion room would explain such a mess.
JMHO
GW0 -
not expansion
Guy, this is a dhw, with no backflow, system is open to city mains.0 -
update
Daryle from kitec was here today. Also talked to Chuck on the phone. Gotta tell you, I could not be happier with the response so far. I wish all reps were like this.
Sample is on its way to the factory. There were no attempts to place blame anywhere, just a sincere desire to find out why.
And yes, we still stock kitec.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements