Pressure sensor at the end of the run?

Would it make sense to add a pressure sensor at the end of a low pressure campus 2-pipe system to help the boilers back in the plant adjust sooner to the drop in pressure? The distance is approximately 1240' from the plant. The end of the run also happens to be a dorm and kitchen area which causes a spike in the steam usage. Any suggestions?

Comments

  • Steamhead
    Steamhead Member Posts: 17,384
    That should work well

    but I'm sure you know that this would be an operating control rather than a high limit. You would still need the normal high limit at the boiler.

    The proper control to use would depend on the pressure you carry.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting