Lochinvar Knight for a commercial application
Kal Row
Member Posts: 1,520
have a job where i had originally speced out a wall of WM ULTRAs but the builder is adamant about no aluminum boilers (there is lots of ignorance out there), and there is no room for a large commercial modulating boilers like raypak/laars/rbi, so I am considering 2x105 knights for the radiant load, and 4x399kbtu knights for the hot water/air handler loads,
I am using a turbomax 109 for hot water generator since with 687000btu input it will give full flow water at 110f from 40f street temp (may add a knight storage tank to that setup for economy in light loads) and the knights also vent to 100ft, i cant just go out the wall since the vent area is at an inside corner and by law I have to go up
So has anyone done this or am I pioneering here? Any knight experience, good or bad would be appreciated
Yes
I think the Knights would be a great choice. Plan on using the internal sequencer to stage, rotate, and modulate the boilers. (...If there is not already a BMS, there are contacts for BMS if the system is in place.)
I need to post some final pictures on another thread. I will bump that thread so you can see. Read the manuals and get a good electrician that can be flexible with your needs.
Regards,
PR
Knight is a great choice. Go for it. We've been very happy with our Knight installs.