Dual boiler P/S piping ?
Gary Jansen_3
Member Posts: 1
Did we ever find out what program he used to do the drawings? Thanks, Gary
0
Comments
-
Dual boiler P/S piping ?
Hi Wallies,
I was thinking of a possable P/S piping arangement for dual boilers to prevent too high of return temperature (and short cycling) to the second boiler when both are firing.
I was thinking of 4 closely spaced Tees with the first boiler on Tee 1 and 3 and the second boiler on Tee 2 and 4. Would this work without interaction?
Thanks
Ron0 -
Instead...
WHy not pull one set of tees of the primary and feed the two boilers in parallel off of that. Then they'll both see the same return and supply water temps.
Don't forget to provide some means of low temp protection for the boilers.
ME
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
And don't Forget
check valves on each boilers outlet. If only one boiler pump is running, a large amount of water can backflow through the off boiler. Also, you want to pump the boilers individually so that you don't get cold return water pumping through an off boiler and mixing down the temp of the hot water coming off the on boiler.
Boilerpro0 -
Here is an example of 5 boilers
in a parallel primary loop. This is essential especially if they are condensing boilers. Definately want to read "Radiant Precision" from the RPA and the mind of John Siegenthaler.
Regards,
PR0 -
Hi Mark,
The reason for thinking about the 4 Tees was to use a pre-made copper manifold for the Tees.
Flo-checks of check valve circs. would be used of course.
Thanks,
Ron0 -
I see...
Well then I guess you could do it like this then...
ME0 -
ya thats the way we do them
with tekmare outside controller and twinning control to cycle each boiler equally so primary boiler is switched back and forth between the boilers.0 -
What about
this?
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Hi Mark,
That's exactly what I was thinking of doing. When "thinking like water", I think it will still work even if there is some difference in restriction and flow rate between the two boilers.
Ron0 -
Ron
0 -
This place really is remarkable!!!!!!!
One question is answered with several smart and viable options. Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Nice drawing Brett..
whose program?
ME
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Negligable...
just make sure you put checks on the outlets of the pumps serving the boilers.
ME
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Question for Brett
Very nice schematic Brett! I have a question. If P4 is a variable speed injection pump serving the secondary loop for the three radiant zone pumps, why not just close the boiler loop and draw off the boiler loop with the injection pump (and DHW or "hot zone" pumps)? That would eliminate the need for the primary loop shown near the top of your schematic. I think Hot Rod's schematic shown above may be a more straight-forward and less expensive way to perform the task. Maybe I'm not understanding your schematic. What am I missing here?
Thanks.....Bob Knebel / Radiant Engineering0 -
In that drawing, both boilers
are seeing exactly the same temps. AND if one boiler springs a leak or goes down for any reason you are not SOL......
simply valve out the offending boiler and at least you can run on one. Also with that drawing you have the potenial to run two different temps. One high temp say for baseboard and one low say for radiant.
Floyd0 -
Hey Brett
what did you use to make the cool drawing??0 -
Visio
He is using the same Visio (Microsoft) program that I use. It also looks as if he has a disc of stencils from Wirsbo that are very nice to construct these pictures with.
Regards,
PR
Paulr@biggerstaffradiantsolutions.com
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements