Are there any shutoff flanges on the zone pump, a pic of your piping might be in order here too

Comments

  • Karl_5
    Karl_5 Member Posts: 6
    gravity retrofit

    I've got a oil boiler that is getting too cold of return water on a gravity retrofit. The bypass is located on the discharge side of the pump coming off of the branch of the tee. The bypass doesn't change anything, its wide open. I read the weil-mclain install book and there isn't valves in the places they tell you to put them. I guess I'm going to have to install a valve to throttle back the supply to the zone. The boiler is a cold boiler. If I switched it to a hot boiler do you burn more oil than if it is a cold boiler. It did run for an hour before it reached 170 degrees.
    Thanks for your input
  • Big Ed
    Big Ed Member Posts: 1,117
    System By-pass

    A system by-pass returns supply water back to the boiler to help prevent thermo shock...

    If the circulators are pumping away from the boiler ....The system by-pass tees after the circulator back to the return .

    If the cirulator is pumping to the boiler.....The system by-pass tees before the circulator from the supply....

    I would pipe a single zone ,non hot water gravity boiler...... cold start , no flowvalve with a B aquastat...

    Assuming that the boiler is sized to the heat loss of the structure....The slow low temperture will add to the comfort...

    A out door reset would add even more comfort..