How many square feet of CI radiation can pex handle

Unless I know:

1) The size of the CI radiation (in EDR)

2) The heat loss [requirement] assocated with such radiation.

3) The expected average temperature of such radiation.

Comments

  • How many square feet of CI radiation can each of these sizes

    handle based on the chart I have from an earlier question:

    3/8 Pex= 5/16" .3125" 1.6 gpm

    1/2 Pex= 7/16" .4375" 2.3 gpm

    5/8 Pex= 9/16" .5625" 3 gpm

    3/4 Pex= 11/16" .6875" 3.67gpm



  • Same question, different approach

    How many BTU/h can I pump through the different sizes of PEX? So I know how much radiation I can stick on the end of the run of PEX. I don't need exact, just something close. I don't think PEX will push the same amount as copper, but I may be wrong.
  • You could push MORE thru pex than copper...

    It's SMOOTHER!

    Delivered btu's on the other end depends upon your desinged delta T.

    Think wide delta T with cast iron radiators.

    Like 30 to 40 degrees F.

    gallons X pounds X delta T X time = btuH

    So, 2.3 X 8.33 X 40 X 60 = 45,981 btuH

    If each square foot of radiation deilvers 180 btu/sq ft /hr, then your 1/2" pipe at 2.3 GPM and a 40 degree delta T would carry approximatley 255 square feet.



    ME