Oil tank vent
Ron Schroeder
Member Posts: 998
NFPA31-2006 is now out and the vent size was changed back to 1-1/4" in NFPA31-2001. I would also always make sure the vent is as large or larger than the fill
An ineresting read, wait a few seconds after the link page is loaded in your browser, and you should be taken to the correct spot on the page.
http://www.steeltank.com/library/tanktalk/vol151.aspx#fire
An ineresting read, wait a few seconds after the link page is loaded in your browser, and you should be taken to the correct spot on the page.
http://www.steeltank.com/library/tanktalk/vol151.aspx#fire
0
Comments
-
Oil tank vent
I know that it is O.K. to have a 2" fill and a 1&1/4 vent pipe. Following that logic, the vent is 3/4 smaller than the fill. At my house the fill is 1&1/2 and the vent alarm is 1" but after the alarm the installer reduced it down to 3/4 for the run to outside. So, my vent is also 3/4 smaller than the fill. The distance from the tank to outside is only about 3 feet. We don't have any local codes in my area ( farm country Wisconsin ) This wouldn't meet codes back east by most of you I am sure, but I am just wondering if I should be worried about tank pressure while filling? I watched the fill, and the whistle stops very quickly after the fill. Are there many 3/4 vents out in the field?? Is this situation an unreasonable risk?? Thanks, guys!! Regads, Jason.0 -
I believe that NFPA-30
as a reference standard if not a code, stipulates a 1-1/4" vent for oil tanks as a minimum size up to 660 gallons, IIRC.
It is not the difference in diameter to the fill but the area of the pipes for venting purposes.
Key to the vent size is to relieve pressure when filling and draining. The tank is not a pressure vessel or more to the point is a limited pressure vessel, generally not over 5 psi. If your vent were clogged (mouse, spider or wasp nest) you could be at risk. (Hypothetical, I know). But the point is a small vent is more likely to clog.
Does what you have work? Apparently. Is is to an acceptable standard? Not in my opinion.
My $0.02,
Brad
p.s. No codes in local Wisconsin farm country? Such lawlessness0 -
Very few 3/4\" vents where I am
The 3/4" reduction logic doesn't hold because the oil hose nozzle opening is either 1 1/4 or 1 1/2". Since on an oil delivery, you are venting air and not oil, you have witnessed no problems. The older the tank gets and the possibility of the tank being overfilled....well??? thats where the problems may come in, especially if the vent cap reduces the venting capacity further.
I wouldn't leave it like that.0 -
I agree with equal size
vents to fill. Much more peace of mind.
What had the vent size been before being restored to 1-1/4", Bruce? I cited NFPA-30 (Flammable and Combustible Liquids Code) because of my work supporting emergency generators), although 31 is more specific to home heating. I thought as far as vents they were congruent; I will have to check.
Thanks
Brad0 -
Brad
Thet had gone to 2" vents with 1 1/4" fill, had to do with some crossover mishaps but after the studies were done they reverted back.0 -
Thanks, Bruce
I knew you would know.0 -
vent the tank well
it the tank is not a pressure vessel.
tanks should arrive on the job site with a vaccum.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements