Eugene Silberstein 3
Member Posts: 1,380
Smaller amounts of liquid will definitely attack the weaker portions of the compressor first, the valves being right up there.
I always tell my guys to ask themselves "WHY?" when they are faced with a situation. In your case, it might go something like this:
1 - The compressor is operating, but bno refrigerant is moving through the system. WHY?
2 - (after testing the unit) The compressor has defective valves. WHY?
3 - Liquid refrigerant has entered the compressor. WHY?
4 - The metering device was overfeeding the evaporator. WHY?
5 - The thermal bulb was not secured properly. WHY?
You get the picture.
Don. You are absolutely correct to mention that ALL thermal bulbs should be wrapped to ensure that the bulb will sense the suction line temperature accurately.
Some individuals are under the assumption that, as long as the thermal bulb is located with in the confines of the air distribution system, the bulb does not have to be insulated. Such could not be further from the truth.
The evaporator is able to absorb heat becasue it is at a temperature that is lower than the air passing through the coil. The suction line is also at a temperature that is lower than the air passing over the coil. By not insulating the bulb, it will be exposed to a higher temperature and, therfore, the pressure in the bulb will rise. This will cause the TXV to open wide.
Thanks for the great post, Don.
I always tell my guys to ask themselves "WHY?" when they are faced with a situation. In your case, it might go something like this:
1 - The compressor is operating, but bno refrigerant is moving through the system. WHY?
2 - (after testing the unit) The compressor has defective valves. WHY?
3 - Liquid refrigerant has entered the compressor. WHY?
4 - The metering device was overfeeding the evaporator. WHY?
5 - The thermal bulb was not secured properly. WHY?
You get the picture.
Don. You are absolutely correct to mention that ALL thermal bulbs should be wrapped to ensure that the bulb will sense the suction line temperature accurately.
Some individuals are under the assumption that, as long as the thermal bulb is located with in the confines of the air distribution system, the bulb does not have to be insulated. Such could not be further from the truth.
The evaporator is able to absorb heat becasue it is at a temperature that is lower than the air passing through the coil. The suction line is also at a temperature that is lower than the air passing over the coil. By not insulating the bulb, it will be exposed to a higher temperature and, therfore, the pressure in the bulb will rise. This will cause the TXV to open wide.
Thanks for the great post, Don.
0
Comments
-
liquid flood back.
Does it take out the valves first?
A system we put in last summer the compressor would not pump.Found a loose thermal bulb with only one screw and no
thermal wrap on the bulb.
Thats another question why are alot of company not wrapping
the bulb now days?Could be they're walking over a dollar to pick up a dime?
Anyway did nothing to the bulb and charge it up in ac mode
in dail it in.Subcool and superheat in the safe zone.
Then I flip it over to heat to see the superheat plunge to zero.Shutdown unit and tighten down the bulb and wrap it.
The superheat came up and maintain around 15 degree.
Darn it...that two compressor replace thus far this year under warranty.
0 -
What's that saying?
Compressors don't die, we kill them.0 -
Noooooooooooooo
The saying is:
"Old fisherman never die, they just smell that way"0 -
\"Old fisherman never die,
they just smell that way" Hey keep me out of this I didn't do anyting to you ;-)0 -
Nothing personal
Nothing personal, Bruce.0 -
Speaking of TXV bulb placement!!
Quite a few years back I serviced a Lennox split system. Can't really remember if yearly maintenance or problem, but here I am and I take a look at the A-coil.
A second look and again, what is wrong with this picture? That's it the txv's sensing bulb is attatched to the liquid line! I could not believe it. I asked the customer if they ever had trouble with the ac not working right, not that they could remember.
So I move it where it is supposed to be and continue with the check. Everything was fine, I could not believe it!
You just never know what you will run into!!
Don in SEIA0 -
I have never....
I've never heard of that one before...
Although I have heard about the suction line being connected to the condensate drain fitting.
No cooling? Gee... I wonder why... No wonder why they couldn't pull a decent vacuum!0 -
I just had one...
that was always flooding back to the compressor and making a rattling noise that the owner asked me to check 'cause it annoyed him. Well, all it was that the duct tape holding the txv bulb to the suction line was loose, imagine that. LOL Best regards.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements