Eugene Silberstein 3
Member Posts: 1,380
Start and run windings are in intimate contact with each other inside the shell of the motor. When voltage is applied to the motor and current flows through the start and the run winding, an induced voltage is generated. This is the same concept that facilitates the operation of transformers. At any rate, the current flow through the run winding induces a voltage across the start winding. So, when you take a voltage reading across the start winding, your reading will be higher than the line voltage.
This is the same exact concept on which the potential magnetic relay operates.
This is the same exact concept on which the potential magnetic relay operates.
0
Comments
-
Potential Relay Voltages
Hi All!Professor,On 1ph compressors the voltage reading[ on a running unit]on the" C to S "terminals is always higher than "line voltage".What is this higher voltage called?Does this happen on 3ph units ?0 -
> Start and run windings are in intimate contact
> with each other inside the shell of the motor.
> When voltage is applied to the motor and current
> flows through the start and the run winding, an
> induced voltage is generated. This is the same
> concept that facilitates the operation of
> transformers. At any rate, the current flow
> through the run winding induces a voltage across
> the start winding. So, when you take a voltage
> reading across the start winding, your reading
> will be higher than the line voltage.
>
> This is
> the same exact concept on which the potential
> magnetic relay operates.
0 -
Higher Volts!
Thank You ,does this "higher voltage have a name?Saying "higher than line voltage voltage" tends to get stuck in conversation,especially, with electricians,and apprentices. Thanks ,again.0 -
When I was in school, a hundred years ago, we called it Back EMF (EMF is electro-motive force). This voltage is used to trigger the start relay to take the start capacitor out of the loop.0 -
Back EMF
HI Paul,That is what I've called it for Years but in the past 8-10 months some college electrical engineering students have said "NO WAY-OLDTIMER". So ,what is the proper term ?[YOU YOUNG WHIPPERSNAPPER!].GOOD DAY!0 -
They wanted you to stew awhile before they told you? I have no idea. Back EMF works for me. How about winding induced voltage? Or magnetic voltage transferance (I'm making this up, but it could be).
Or Wattage Heat Amperage Transfer Energy Vector Electric Replacement, also known as WHATEVER.0 -
It's Induced Voltage
I though I mentioned that earlier.
Oh well..
I do like the WHATEVER idea, though.0 -
Techman
Tell the young whippersnapper to put one finger on C and another on S while it's running and let HIM tell you what it is.0 -
All wrong
you put (C) Common on his tongue and (S) Start in his ear and ask him to shake his head when the compressor starts. Best Wishes J.Lockard0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements