new high limit failure?
Options
Kal Row
Member Posts: 1,520
they had wired the boiler's 110v supply, to the system demand control - so if the demand was satisfied - the boiler and it's pump was shut of abruptly with no way to purge the residual heat out of it, if it had just gotten to 180, thus the trip I would have seen it right away but its one of those rats nest boiler rooms that make you dizzy just looking at it!!!
0
Comments
-
new high limit failure?
got a brand new IBR 8900 series (630kbtu), that keeps tripping the high limit,
-the high limit (on boiler's discharge) is set for 200f
-the aquastat (on boilers return) is set for 170
-the installed paddle switch is working correctly and indicating good flow
-the system is piped primary/secondary
-the boiler pump has sufficient gpm and head to get the BTUs to the close-T's
-the tridicators on the boilers return and discharge ports never get past 180
-there is no appreciable pressure differential between the two that would indicate a flow restriction
-the system is purged of air
how many of you have experienced a new high limit failure as this would be a first for me
0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements