steam sizing
stupid question time how many installers add a pic up factor when sizing steam boilers I am looking at a job that has 346sq. feet of steam based on the radiators there is 25 ft of 2in steam pipes running thru out the basement all pipes are insulated can I just use the built in pickup factor from the manufacterer?
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=354&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
    EBEBRATT-Ed Posts: 20,934
    Personally I wound not ad any pick up other than the manufacturers already built in 1.33. That's 33% above the load. Why add more??
    Unless there is unusual piping, or a really large domestic load or uninsulated piping (you already mentioned it was insulated) then maybe??
    Chances are if you do a heat loss calc. the building probably has more radiation than it needs to be adequatly heated and the boiler selected probably does not match the connected EDR exactly so.................
    pick-up factor-- plus more radiation than needed--and closest boiler selection larger than connected load= plenty of fudge already. Don't want to be way oversized.
    JMHO
    Ed
  • Ed, go with the manufacturer's
    EDR ratings. Unless you can see that a lot of radiation was removed- then you might want to add a bit for the now-oversized piping.