A fellow tech asked me this question . Call it a 4 zone boiler , circs are pumping away from the expansion tank and fast venting B+G EAS . Pressure around 15 psi . What if all 4 zones came on at once when the low limit is satisfied ? Can air get sucked into the system through a fast venting air eliminator ? Thanks in advance . Ron
0
Comments
-
No.
Retired and loving it.0 -
Ditto NO...0 -
Nope,nope,nope.....0 -
Just to be clear ....
I see a common theme in the responses , thanks guys .
OK , next question . Can air be introduced through the scoop at very low pressure in the same scenario ( all pumps on at once ) ? Could it happen at low pressure with the expansion tank downstream of a circ ? This is to help out a serviceman buddy , so if anyone can elobarate on a response , I'd appreciate it . I have Dan's " Pumping Away " somewhere here but I can't seem to locate it .0 -
Not
as long as the system fill pressure is above atmospheric pressure.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
That's right.
Retired and loving it.0 -
Thanks Frank
That was my answer , the system pressure has to be subzero at the airscoop to introduce air . But he was wondering if multiple circulators turned on at once can bring it to subzero at the scoop if it's close enough .0 -
The reason why this cannot happen is that even on the suction side of the pumps, you still have pressure. A circulator is a pressure differential device, however you must not forget that the hot water boiler should be set to at least 10-12psi and if you were to install pressure gauges before and after the pump you would read a higher pressure on the discharge side compared to the suction side, but there will be some pressure on the suction side. The air purger will never see a below atmospheric (vacuum) condition.... lets assume standard sizing practices were maintained to size the main (primary) piping.
Cosmo Valavanis0
This discussion has been closed.
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 114 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 110 Geothermal
- 161 Indoor-Air Quality
- 3.6K Oil Heating
- 71 Pipe Deterioration
- 999 Plumbing
- 6.3K Radiant Heating
- 392 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 46 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements