What's the best (prefered way) to pipe a low mass electric boile
Options
hr
Member Posts: 6,106
required. Depends on the wattage, etc. Some elements with real high wattage density need flow across them.
As noted above, follow the manufactures directions to avoid problems and potential warranty issues.
hot rod
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
As noted above, follow the manufactures directions to avoid problems and potential warranty issues.
hot rod
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Best way to pipe a low mass electric Boiler
I was just looking for some thoughts on what is considered the best way to pipe a low mass elec. boiler? Any help will be greatly appreciated. It's about 3000 sq. ft. and one zone. Is Primary/Secondary the best or just pipe it boiler supply to manifold supply, and from the return manifold to the return of the boiler.0 -
In general
If you are zoning, you will want to use pri/sec or a differential pressure bypass. Keep the flow rate high through the boiler. And, as always, follow the manufacturer's piping recommendations.
-Andrew0 -
and remember
wire over water.
J0 -
flow is essential
with electric boilers. as above, if you have any kind of zoning at all a pressure bypass or primary/secondary is a must. if the boiler fires with no or too little flow the elements will short-cycle like mad and you will burn out the contacts, which over time can weld themselves closed until boiler blows off all its water and the elements burn out. not fun!
0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 428 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements