Looking for some input on installing a 2 ( 105*, 112*) zone 21000 btu slab radiant - customer has no place for oil or propane heater, as above utility room is a finished roof deck. This is new const, 26 x 42' single floor slab w/ cath ceil most areas,, am thinking Carefree boiler w/ prim / sec w/ 2 zones, tru-flow mainfold, thermostatic mix valves , Total GPM is 2.2 ,, Carefree E412 41,000 BTU cap. Some input please. ( thanks for the help last post, Too much GPM due to a different spec sheet for parts,, MY OWN FAULT- can't be somebody elses?)
0
Comments
-
Personally
I would supply one temperature to both those zones. Add the two required temperatures then divide by two to get an avearge temperature. If both required temperatures are within 10% that's close enough, in my opinion.
Most radiant is built around a 10- 15% delta t anyways.
Also consider a modulating electric boiler. They handle changing loads better. I like the Thermolec as it comes in many sizes and has an outdoor reset feature built in. A lot quieter than thase large contactor types.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements