Wayco Wayne_2
Wayco Wayne_2 Member Posts: 2,479
old dear customers who have a Burnham cast iron boiler about 8 years old. They are retired (and on a budget) and got quite a surprise when their gas bill came this past month. Prices have gone up and December was colder than usual. I want to install an outdoor reset control to help them cut costs but...the system is a 2 pipe with 4 zone valves and one of the zones goes to an indirect water heater. I don't want to burden them with an expensive repipe to make the indirect on a parallel circuit. Is there an outdoor reset that can reset the temps for the 3 other zones but go to high fire when the indirect's zone valve calls for heat?

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=255&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • singh
    singh Member Posts: 866
    check out

    the Taco 700 series. I have not used it yet,but I am very interested if anyone has,like Wayne I have customer that is now looking to reduce fuel costs on a system I installed a few years ago.

    I think integrates into the SR zone relay and have that on priority for DHW.
  • Wayco Wayne_2
    Wayco Wayne_2 Member Posts: 2,479
    Thanks for the reply

    I will check it out. I also think I can use a Tekmar 260 and make it work with a little creative wiring. If I may ask another question... Does anyone have a time clock that they recommend using with the Tekmar controls to initiate the set back contact?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Intermatic

    Makes a simple $30-35 digital timeclock that mounts in a Decora or GFCI style plate junction box. I use it to set back my DHW heater when I am not home and for lighting control. I am sure there are others out there.
  • heatboy
    heatboy Member Posts: 1,468
    Uponor :-) 311................

    ..........will do everything you need WW.

    hb

    www.climatecadvanced.com

    There was an error rendering this rich post.

  • Wayco Wayne_2
    Wayco Wayne_2 Member Posts: 2,479
    Yeesh!

    You have expensive tastes Heatboy. These folks don't need the variable speed. (I think you must be funning me:) I've only installed one 311. Worked great though. I gave the customers a price for the Tekmar 260. Do the Intertherm water heater timers keep good time, or do they lose a minute hear and there. do they have a battery backup. Inquiring minds want to know. WW

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Rodney Summers
    Rodney Summers Member Posts: 748
    you could just hook-up one of the these...

    that's what i did. a prog t-stat is really just a timer with a spst switch - isn't that what you want? (just set it to the extremes so that it ignores temp like 40 or 90f for on & off). plus you get battery back-up & daylight savings time to boot.

    ss
  • J.C.A._3
    J.C.A._3 Member Posts: 2,980
    WW,

    I think the 260 is a fine choice. Does it well and the price won't break the bank. JMHO....Chris
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    Wayne...

    I have a Tekmar 260 on my home and it works very well...Another less complex way I just did is an Argo zone valve control and the DPM-2 outdoor reset control..It does work w/ an indirect water heater on priority....simple yet efective...hope this helps.kpc

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    To avoid the expense of a fancy reset controller why not use a simple one and add a DPDT relay? Have the indirect zone operate a relay that bypasses the reset--that way the boiler will fire to aquastat setting. Once the DHW call ends the boiler will return to the reset setting.

    If you use two 3- or 4-pole (4 pole are easier to find) relays you can easily set up that four-zone system for DHW priority with the space heating zones disabled during a DHW call.

    Let me know if you want simple schematics.



  • Boiler Guy
    Boiler Guy Member Posts: 585
    Grasseilin

    makes an excellent little timer which I have used powered right off the tekmar
  • grindog
    grindog Member Posts: 121
    tekmar

    use the 260 it has outdoor reset and prioritizes when the indirect calls for heat. if you dont want priority use the tekmar 256 will cost a little less if you are on a budget.
  • Jamie_6
    Jamie_6 Member Posts: 710


    Wayne,

    A Tekmar 360 would work fine! You can still use the dry contact with a zone valve.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • EJW
    EJW Member Posts: 321
    Taco Outdoor reset

    Singh, it does work with the SR but it needs to be the SR expandable control. This control also takes the plug in cards for more options. EJW
  • Kniggit
    Kniggit Member Posts: 123


    We have installed three 700 serires two two stage and one single stage. if you have a SRxxx-EXP or ZVCxxx-EXP end anyway they work great, my bigest gripe about the Taco controlers is having to carry a tiny screw driver.
  • Joe Mattiello_2
    Joe Mattiello_2 Member Posts: 94
    Taco ZVC404-EXP

    The Taco ZVC404-EXP is an excellent candidate for your application. It is a great facilitator for wiring your system, two 40 VA transformer to power the valves, diagnostic lights for troubling shooting, dry contacts for optional circulator dedicated to domestic water, two isolated end switches for firing the boiler, and running a system pump. The PC700-2 outdoor reset control will interface with the 404-EXP by simply plugging it into the Molex connector. For your reference I have attached product information. If you have any questions contact me directly, or visit www.taco-hvac.com.

    Joe Mattiello
    Technical Support Technician
    Tel. 401-942-8000 X 484
    Fax. 401-942-2360
    1160 Cranston St
    Cranston, RI 02920
    joemat@taco-hvac.com
  • mark schofield
    mark schofield Member Posts: 154
    honeywell OA boiler trmp reset control

    Honeywell part# AQ475A1004
  • Rookie
    Rookie Member Posts: 175
    Taco 700 series

    Wayne I would take a look at the Taco 700 series control, we use them and have had excellent performance from them, and their product support is excellent. We have also used Tekmar and have had nothing but positive experiences with their products, the customer support with Tekmar is also excellent, Taco is readily available(more than Tekmar) over here on Grapeland. Good Luck.