No Circulation

Joerg
Member Posts: 1
I just had a new circulating hot water heating system installed. It has 6 zones with individual Taco 007 circulators on the supply side. The system pressure was set for 12 psi. When tested the zones on the 1st floor worked fine, however those on the 2nd floor did not. The Pex piping rises up to the roof ( 26 ' ) and then down into the radiators on the 2nd floor. The radiators had been vented.
We raised the system pressure to 25psi however the water was still not circulating. What could cause the problem and how could it be solved?
Any help is greatly appreciated.
Joerg
We raised the system pressure to 25psi however the water was still not circulating. What could cause the problem and how could it be solved?
Any help is greatly appreciated.
Joerg
0
Comments
-
NO CIRCULATION
flo checks are open? or system is air bound.rusko0 -
There should be purge
cocks somewhere in the system?? I generally locate mine right at the pump iso flanges. You may have to do one loop at a time, and a fast fill fill valve speeds up the process.
Once the air is purged make sure the pump is powered AND spinning. A stuck impeller is another thing to check.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
26' is a high lift you want to check the chart that comes
with the pump you might be looking at a 008
i don't have one with me maybe some else does0 -
Static pressure does the job of lifting in a closed hydronic system. The circulator merely circulates.
12 psi will lift water about 27.6 feet.
You might want to temporarily install an accurate, low-reading pressure gauge at the high point in the system. On a system of this height you should read 1 - 1 1/2 psi with the system cold and the circulator off.0 -
not meaning to depress you ....
a circulator installed backward does a mighty fine job of not getting the job done,...from time to time.
something else that may help though, if you put in the circs, is back purging ,once you have established flow in one direction. .......if you have checks ,in-line , then give them a tap with a small beater stick and lossen up thier memory cells *~/:)0 -
\"The Pex piping rises up to the roof ( 26 ' ) and then down\"
Bet that's where your problem is. Unless there are vents up there it's a perfect place for air to get trapped. You may have to have vents installed if the usual purge method won't work.0 -
IFC ?
Perhaps the Pump has an IFC forced close when purging the system?
Taco, Inc.
Joe Mattiello
Technical Service Technician
joemat@taco-hvac.com
401-942-8000 X 484
www.taco-hvac.comJoe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
Steamhead is on to something
find that highest loop, install a tee and bring a tube down to where it can be purges with a hose bib on it. That high point loop may be a air lock problem every fall. Air will always make it's way up there over non use periods.
We used to drill into the copper pipe and solder a 1/4" soft copper tube. Drop the end down into an easy to get to space, and install a small valve for purging.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
i still say change the pump
had the same problem on a hydro coil in an attic
changed to 008 never came back in over 2 years now0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 949 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements