Primary/secondary hydronic piping and elbow proximity

We use 6 pipe diameters as a rule of thumb for spacing from elbows or other turns away from the tees, on either side. we've not had any problems. We just did a big TACO Load match systme with 24 zones, had to really pack in the manifolds in a tight space, and it works fine.

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=248&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Mike Ostrowski
    Mike Ostrowski Member Posts: 1
    Primary/secondary hydronic piping and elbow proximity

    Hi,

    I have a hydronic piping question.

    My question revolves around the proximity of an elbow in the primary loop to the secondary supply piping. Is there a distance that an elbow in the primary loop should be away from transistion tee at the connection to the secondary supply piping?

    I am having some flow problems and I thought that the flow may be inhibited by the closeness of the elbow to the secondary supply piping.

    Please let me know what you think.

  • hr
    hr Member Posts: 6,106
    It's nice to have some distance

    at least a 6" distance. Although many of those prebuilt panels, and prebuild hydronic control boxes have fittings and valves jammed right against one another.

    What type of problem are you having? A tight turn right after the takeoffs may induce some flow in that secondary. Same with takeoffs that are too far from one another.

    Generally you want a flow check or two, possibly thermal drops on those secondary takeoffs, to prevent thermal migration (ghost flow)

    hot rod