Staple up issues
RadPro
RadPro Member Posts: 90
do I need to run temp in the staple up application at least 20 degrees hotter to have effective heat on a thick hardwood floor or can I add a third loop between the floor joist for mor BTU's on tap.... Paul
  • You need to do the heat load calc, see what output you need, and check it against your method's output at a certain R value floor covering.
    Adding a third loop will do nothing for you.
  • bill clinton_3
    bill clinton_3 Member Posts: 111
    yes and yes
    Assuming you're talking about a bare tube staple-up; yes you need to run higher temperatures as compared to plates or above the floor methods. Whether 20 degrees will do it, I can't say. And, yes: a third tube will increase heat output--but not by 50%. Again, I cant say how much the increase would be with any scientific backing, but my seat of the pants guesstimate is 20--25%. It's a diminishing returns thing: A fourth tube might net you 10%-15%. When you get to six tubes the whole thing resets and goes back to zero :)
    Bill
  • RadPro
    yes I would be using plates
    but its a thick plank floor 1" over the 5/8" subfloor so there will be major lag time to get the Btus up thru the floor... .Thanks Paul
  • You'll still have a time lag with staple-up. Most likely a significantly longer time lag... Conduction trumps radiation and convection every time! Sure hope your btu/hr per square foot load is low (e.g., VERY good insulation and infilatration control)!!!!!!!!! I'd start getting quite leery if you need more than 20 btu/hr per square foot of heated floor area. Area rugs will be an absolute no-no!