Burnham V13A oil boiler
Actually, there is no chamber in a V13 boiler. There are three seperate components that line the inside of the chamber. They are the rear target wall insulation, chamber blanket and burner mounting plate insulation. I will post the Burnham part numbers for these late this afternoon when I return.
Glenn Stanton
Manager of Training
Burnham Hydronics
U.S. Boiler Co., Inc.
Glenn Stanton
Manager of Training
Burnham Hydronics
U.S. Boiler Co., Inc.
0
Comments
-
Looking for a service manual for a Burnham V13A oil fired boiler or info on replacing the chamber. Brian0 -
Nice boiler
chamber is a Lynn #1064. Which burner does it have?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Part Numbers
Here are the parts you need to replace V13 chamber components.
# 8202701 - V1 Target Wall
# 82022033 - V13 Chamber Blanket
# 8202210 - V1 Burner Mounting Plate Insulation
Glenn Stanton
Manager of Training
Burnham Hydronics
U.S. Boiler Co., Inc.0 -
Also
The 1064 Lynn Chamber is actually a chamber kit and should consist of these three components also, although I'm not so sure of the Burner Mounting Plate Insulation being included in that kit.
Glenn Stanton
Manager of Training
Burnham Hydronics
U.S. Boiler Co., Inc.0 -
It is, Glenn
I put one in my V-14 and it included all three pieces. Didn't know you could still get them from Burnham.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thanks for the info. I've got the part numbers. Wondering how to access the base of the boiler. It does have a door like the other boilers I've worked on. Service manual would be great. Just wont to know what I'm up against before I do the repair. Brian0 -
DG
1. Can I use the C3 I&O manual for my V13AT boiler?
I see the C3 specs of
Firing rate (0.75 GPH)
DOE htg cap (89 MBH)
and Water (77 MBH)
are the same as on my V13AT boiler and the picture seem very similar too except for the burner mounting plate.
2. What are the differences between the two boilers?
3. The C3 manual recommands 1.25" piping for supply and return.
Is it OK toI increase it to 1.5" to reduce the head loss? (I want to use Taco 007)
Thanks0 -
pretty much the same boiler
I would stick w/ the 1.25" header. The 1.5" would be overkill. How many zones? how lond is each zone? What is the Application? That would determine your circulator size.....kpc0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements