Dole 1933 as Mains vent?!?!?
Options

Cast Iron
Member Posts: 35
Anyone think I could just stick a Heat Timer Varivalve on there as a Main vent?
0
Comments
-
Dole 1933 as Mains vent?!?!?
So I read Dan's 'We Got Steam Heat' and I ordered the venting capacity chart and am trying to get my single pipe steam to work as well as possible. It's actually a very quiet system.
Here is the strange thing though. When I went to look at my only main vent in my basement, I found it to be a Dole 1933- Isn't this for radiators? Any idea why this would be the case? Can I just replace it with a mains vent? It's a short 2" 18' main.0 -
Definitely undersized -
Funny - I had the same exact situation in the home I recently bought. Found out from here that the 1933 is designed for a convector. When I first fired up the boiler for heat, the main took 8-10 minutes to fill with steam, and I wasn't getting positive shut-off from the vent. My main is 32ft of 2" pipe. Since I replaced the 1933 with two Gorton #1s, my main fills and the vents close in 1-2 minutes. A big difference. Wasn't in the house long enough to compare fuel use year over year, but I'm sure that alone made a big difference.
Best regards,
Sean0 -
Great, thanks. When I removed the Dole the main filled in 3 minutes from when the header got hot, but like yours, the Dole wouldn't close until the system was on for quite some time.
0 -
On a short main like yours
vent it with a Gorton #1 or a Hoffman #75. These have 1/2-inch female and 3/4-inch male threads, so if your 1933 had smaller threads you will need to remove the bushing it was screwed into.
Is this the only main in the house?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
There are no other main vents. That was what I was wondering, the 1933 has smaller threads (similar to the size going coming out of a rad), so I wasn't sure how to attach the bigger vent. Basically, they attached a smaller pipe coming out of the end of the main.
I'll take a look to see if I can remove this short piece of little pipe the current 1933 is attached to.0 -
If they drilled and tapped 1/8\" threads
into the side of the main, get a Gorton #D radiator vent. It does about as well as the two main vents I mentioned earlier.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Here is a link to a place where you can get Gorton D's with a 1/8" straight shank:
http://www.pexsupply.com/index.cfm/action/catalog.browse/category_header/1/id_category/9ad86cb1-ac62-4f4d-a73b-594633b64ccc0 -
Great, that's what I need. The straight shank, not angled.0 -
I wouldn't
the Vari-Valve has no float, so if water backs up into it it will spill out of the vent. Use the Gorton.
"Steamhead"
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Great,
Thanks to all of you for your advice. It's quite helpful.
Gorton # D it is!!!0
This discussion has been closed.
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 116 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 109 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 984 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements