Tapping a Radiator

bob young
bob young Member Posts: 2,177
start with a 1/8 " pilot hole . then the exact correct drill that matches tap size. very slowly.

Comments

  • USA498
    USA498 Member Posts: 45
    tapping a radiator

    I would like to know if there are any tricks to tapping a new hole for a additional vent in a very large and mostly cold radiator. I already have a Gorton 'D' on it but only 4 out of the 20 or so fins gets warm after a 1 to 1.5 hr run.

    Many Thanks !
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    I've tapped a number of rads from steam systems for water use. Seems to be very easy as the cast iron drills and taps very well. I drilled slowly and used plain cutting oil when tapping.
  • USA498
    USA498 Member Posts: 45


    Did you have to start with a small bit and work your way up ?
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    Believe that's exactly what I did. No joke about the exactly correct drill size.
  • Bob W._3
    Bob W._3 Member Posts: 561


    My 1/8 - 27 NPT tap specifies a 21/64 drill bit, which seems to just fit in a 1/8 female fitting. Not sure what the outer diameter of 1/8 pipe is; depends on the type of pipe.
  • USA498
    USA498 Member Posts: 45


    Thanks for the info.
  • Tom R.
    Tom R. Member Posts: 138
    Pipe size

    1/8" pipe is all the same O.D. - wall is thicker on sched. 80
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    Are your main vents big enough?

    A gorton D is equal to the largest main vent avialable except the Gorton #2. Also, does your boiler have a nice long on cycle?

    Boilerpro
  • USA498
    USA498 Member Posts: 45
    Tapping radiator

    Thanks for the reply.

    The Main vents are gorton #2's located at the end of the return ( about 16" back from the end ). The Gorton D is on the ratiator that is slow to heat. I can only get about 4-5 fins out of 22 to heat on a pretty cold day. The firing time is approx 1 to 1.5 hrs. I thought a second vent might do the trick.

    Thanks again
  • Bob W._3
    Bob W._3 Member Posts: 561


    Probably will, but if you can vent the riser to that rad it would be even better.