muffled Bud

Unfortunately there are times chimney noise occurs( sounds like a loud "roar" usually from the chimney. This has occured with mostly Riello burners, but also with Carlins, in chimney's of all types. Sometimes a nozzle change has helped and other times a liner. There is no set pattern that we have seen to cause this. The noise is caused by sound waves, generated by the burner, travel through the boiler and resonates when entering the chimney. The muffler install looks good. Would like to see better photos if possible. Thanks

Comments

  • Dave Palmer_3
    Dave Palmer_3 Member Posts: 388
    first

    replacement with new company. Swap-out ,but had to install muffler on boiler,kind of a pain to do but worked great.Boiler was very quiet.Dave
  • Darin Cook_3
    Darin Cook_3 Member Posts: 389
    Dave

    What kind of burner is on the Buderus? I have never had to use one of those mufflers yet, they always seem very quiet as is with a Riello. Can you post some more pics? The work looks nice from what I can see.







    Darin
  • Dave Palmer_3
    Dave Palmer_3 Member Posts: 388
    Reillo

    was the burner.Burner made more noise than exhaust up the chimney.I'm going to save my pennies to put one on my Viessman.Sorry the photos are so big,I did a crappy job resizing.
  • Weezbo
    Weezbo Member Posts: 6,231
    we were going to put a couple on the7 section