Gorton Vents
Steamhead (in transit)
Member Posts: 6,688
should each have one Gorton #2. The dry return would need one #2 also. So you want to buy a total of three.
"Steamhead"
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
"Steamhead"
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Number of vents needed
Please advise on the number of vents needed for an old vapor system. I have a total of 118' of 2" ID supply, I want to order the Gorton #2's and not sure if 1 is ample or should 2 or greater be installed. Then what about the return side which is 1" ID? Currently this is the most active of the 2 original (Moaut) vents. Thanks for all of your help!0 -
Is the 118 feet
all in one main, or is it split between two or more mains? If the latter, how long is each main?
For the returns- how many radiators does your Mouat have?
"Steamhead"
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thanks Steamhead
Two mains, one being 57' with 5 radiators and the other 61' with 8 radiators. Total radiator square footage is 606.
I also am concerned with the height needed for the #2 Gorton vents. I have 12" above the supply line and 16" above the return line. Is this enough height, or should I consider the #1 Gorton vents instead. Thanks again!0 -
61' of 2" = 1.33 cu. ft.; you would need 2-3 No. 1's or 1 No. 2.0 -
With 12 inches above the vent tappings
you have plenty of room for one Gorton #2 on each main. That's what I'd use. Bob did the math.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Steamhead, Just to clarify you are saying two #2's at the end of the supply line. Then what about the return, two #2's there also? Thanks!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements