Returns-dry to wet conversion

Jim B_2
Jim B_2 Member Posts: 20
All:

Planning a basement re-model and would enjoy having the extra few inches of headroom taken up by the dry return lines. I am considering converting to wet returns and running along the basement walls. I would apppreciate any comments or concerns wrt to doing so.

Thank you.

Jim B.

Comments

  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    I don't foresee any problems

    go for it. A 1-inch wet return will handle 700 square feet EDR- more than the same size dry return if memory serves.

    If you don't have main vents, now would be a real good time to add them.