Indirect Domestic Hot Water
Constantin
Member Posts: 3,796
I'd pipe the tanks in paralell to minimize the possibility of stacking. I presume that the boilers do more than just heat hot water and the quick sketch I threw together reflects that.
Have you tried contacting Monitor? What do they recommend?
Legend: AS= Air separator. Also a good location for the expansion tank. Note the reverse return configuration for the indirects. That way they both get the same flow of water. Cheers!
Have you tried contacting Monitor? What do they recommend?
Legend: AS= Air separator. Also a good location for the expansion tank. Note the reverse return configuration for the indirects. That way they both get the same flow of water. Cheers!
0
Comments
-
Domestic Indirect Hot Water
Trying to figure out the best way to pipe indirect system using 2-MZ 40 Boilers, 140,000btu and 2 50 gal. indirect tanks. Wondering if it better to hook tanks up parallel on the domestic hot water side or in series?0 -
You should also reverse return the DHW in and out.0 -
Very good point....
... and thanks for pointing that out. The error has been corrected in the diagram but does the rest of it make sense?0 -
You know me
Mister energy mizer. With this you can't get anything but a balanced and even flow. With minimal power consumption.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements