1/2\" convector in 3/4\" zone

hr
hr Member Posts: 6,106
pipe it with a bypass and a ball valve for flow regulation. 3/4 x 1/2 tee, then a 3/4 ball or globe valve, then another 3/4 x 1/2 tee. That is IF you have access to the valve to adjust flow.

hot rod

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Jim Franklin_2
    Jim Franklin_2 Member Posts: 70
    1/2\" convector in 3/4\" zone

    I bought a kickspace heater for the kitchen. It's plumbed in 1/2" (about 4' total) but the zone will be 3/4" and 4 GPM. Is this a bottleneck worth dealing with? The spec sheet lists a pressure drop of .422' @ 3 GPM and 1.026' @ 5 GPM (it'd be nicer if they just gave me a curve) - is that small enough to ignore in a 150' run with several turns and 3 convectors?

    If I need to deal with it, what are my options?

    thanks,
    jim
  • Ted_9
    Ted_9 Member Posts: 1,718
    heating

    You should pipe it with one regular tee(3/4x3/4x1/2) and one monoflo tee(3/4x3/4x1/2).
    The first tee is reg. and the second is the monoflo.
    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • WPH2205
    WPH2205 Member Posts: 52
    Hot Rod

    Hot Rod is 100% correct. Pipe it just like he suggests. I've been doing them like that for 15 years.
  • Jim Franklin_2
    Jim Franklin_2 Member Posts: 70
    thanks

    I was hoping the monoflo would be a solution, given the simplicity, but now that I think about it the balancing valve is probably better from a "system" perspective. The kickspace heater will be in the corner of an L shaped kitchen with an island, so being able to control it would be nice, like turning it up for morning coffee but down for ovens-blazing Thanksgiving, though that might be putting too much faith in the homebuyer. Hmmm...maybe a TRV on the rad piping and leave the bypass open? It does have a normal-off-boost switch for the fan motor though.

    Gah. This design stuff really sucks one in. It won't be my house. I'll put in a balancing valve with a note on it and call it good. :-)

    jim
  • Jay_17
    Jay_17 Member Posts: 72
    One more idea

    I did this in the same situation, I added a 110V thermostat in the kitchen which controls when the fan is allowed to operate, a simple and cheap way to make a zone.
    Jay
  • RMA
    RMA Member Posts: 55
    kick toe

    MONOFLO