there is a way to hook more than one slab sensor up to a tekmar thermostat but I cant semm to rember it , I thought that there should be 3 sensors wired in series to produce the same result as 1 sensor but the ohm reading is not right for this when i put the 3 to gether I get the three added to gether and dont get the right readings , they covered this in a tekmar course about a year ago and now that I need it I cant seem to rember the correct sequence any help would be apprecitated. thanks guys!

Comments

  • Empire_2
    Empire_2 Member Posts: 2,340
    Tekmar

    CHeck out Tekmar controls.com/......Everything you need should be there. Just an added thought,..Averaging sensors which you are applying to this job should be wired in parallel. I am not sure what control you are using, but the terminal block has to have the ability to average the total sensors you are using be it 3/ 5/ 7 /9 etc...