Draft Question
Mike T., Swampeast MO
Member Posts: 6,928
Old house. Tall (40') unlined, multi-chambered, brick chimney originally designed for coal burning. Flue unobstructed and in good shape for something 100 years old.
Now all natural gas.
Only thing running in warmer months is the stand-alone water heater.
In some weather conditions, air flows down through the chimney and you can smell the water heat pilot. Cigarette confirms the negative draft but also shows good draft is established about 20 seconds after water heater fires.
Normal? Reasonable? Danger? Another good reason to use an indirect off the Vitodens?
Now all natural gas.
Only thing running in warmer months is the stand-alone water heater.
In some weather conditions, air flows down through the chimney and you can smell the water heat pilot. Cigarette confirms the negative draft but also shows good draft is established about 20 seconds after water heater fires.
Normal? Reasonable? Danger? Another good reason to use an indirect off the Vitodens?
0
Comments
-
With the phrase-
"Another good reason to use an indirect off the Vitodens?"
I'd say you've come up with a good workable solution. That's what I'd do. Any downdrafting can be dangerous. What if the downdraft doesn't reverse? It only takes one time....
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Chimney
The old coal fire had a much higher stack temperature than the NG combustion. All that heat kept the chimney nice and warm and condensation free. With the lower stack temp. of the gas unit, the chimney gets and stays cooler, resulting in lower draft and downdrafts. The resulting condensation is acidic from the flue gasses and will deteriorate the mortar causing loose and falling bricks or stone and general chimney degradation. I would line the chimney with a stainless steel liner and insulate with vermiculite. Or- Go direct vent or- indirect if the boiler is not using the same chimney.0 -
Must Say I Agree
Even if this has been the norm for at least 60 years.
Just kind of glad that the basement has 5 doors and 6 windows...0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements