Richardson System Venting

B. Tice
B. Tice Member Posts: 206
What would be a good air vent to replace an original Richardson tee style main vent? Very few vapor/vacuum systems around here so I'm a little in the dark on venting the mains on these type systems.

Comments

  • Steamhead
    Steamhead Member Posts: 17,564
    That was a classic system

    but if the vents have never been changed, it's probably still set up for coal firing.

    With automatic firing- oil or gas- you need more venting capacity, and you need venting on the ends of the steam mains as well as the dry returns where the original vents were.

    I think the closest match for the original Richardson vents is the Gorton #2. For the steam mains you'll have to measure them out to see how much air is in them. Then go to

    http://www.heatinghelp.com/shopcart/product.cfm?category=2-138

    to buy a copy of the latest info on vent capacities- with the proceeds going to charity.

    You may have to drill and tap the ends of the steam mains to vent them, but it's worth the effort.