steam boiler short cycling
Dave_22
Member Posts: 232
A friend recently bought a house with steam heat. When I went down to watch it, it short cycled constantly on the low water cutout switch. I'm not too familiar with a steam system-any ideas??? It's a one pipe system and the boiler was replaced 4 years ago. Thanks.
0
Comments
-
steam heat short cycling
what is pressuretrol set at? is it gas or oil? is it the right size for the house
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
not sure about the pressuretrol. It is gas and I have not done a heatloss so I am not sure about the load. Looking at the gauge,if it works, showed under 1 psi.0 -
short cycling
on the LWCO may have little to do with more than adding a bit of water. After the boiler has been off for 10 minutes or so, where is the water level? Still near the CO?0 -
Yep, or could be
a dirty boiler too. Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
no- it seems almost as soon as the burner shuts off it comes up midway on the site glass.0 -
are the returns dry or wet? if wet they may be plugged and slow to return. Causing the cycle of low water
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
OK- Now I am at the point of being confused!!! What is dry or wet returns??0 -
Dry returns are returns that are above the water line, wet are below it and full of condensate all the time. Wet are sometimes under the floor or on the floor.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
short cycle-steam
Check your pig-tail it maybe plugged which will cause short cycling.
0 -
not sure if it had a pig-tail, it been a few months since I looked at it. I think I need to study steam heating a bit more!!!!0 -
Dave, it sounds to me like a near-boiler piping problem. If the boiler is not piped properly with a correctly sized header, equalizer, and Hartford loop, when the boiler makes steam, the water will back out the bottom of the boiler and into the returns. this will cause the water in the glass to drop and the boiler to go off on a low water condition. When the burner shuts off and the pressure goes down, the water comes back in and the burner turns on again. Check the piping. Also I agree with the post above- it could also be a dirty boiler. May have to be skimmed and cleaned. But I don't think it's the pigtail on the pressuretrol. My experience with these is when they block up, the burner will run until it gets steam up, then shut off and not come back on. Good luck.0 -
Thank you all for your help. I will take these thoughts with me when I go to have a look. Also, thanks for your patience in helping me understand steam a bit more!!!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements