condensing boiler
Keith_8
Member Posts: 399
piping takes care of that. The boiler operates at non-condensing temps. The building loop maintains @ 95*.
A condensing boiler would seem to be a no brainer.
The boiler can modulate and stay on cruise control.
Keith
A condensing boiler would seem to be a no brainer.
The boiler can modulate and stay on cruise control.
Keith
0
Comments
-
modulating gas burner
Looking for some feedback on a modulating gas burner/boiler used in a heat pump application.
I'm doing a boiler survey this week. The building uses a Raypack boiler to maintain 95* water temp for their heat pump loop in the winter.
Any thoughts?
Keith
0 -
Hummmm~~~~~~~~~~~
Yes, a thought ! I'd hope the water gets hotter than that through the raypack, as condensation will be a factor. Check with Raypack for the specs and make sure they fit the application. excess water in the combustion chamber is really not good. Anyhow, bigugh0 -
What size?
What are the flow rates needed? Viessmann Vertomat has no flow restrictions and would be around 96% combustion eff. at that water temp.
Ted
Viessmann rep.0 -
I'll know
on Wednesday. If I remember correctly about 800,000 MBH.
96% sounds good!
The Raypack is probably closer to 80% efficiency?
Keith0 -
SB series Condensing boiler
We dont require any particular return temp. The lower the better. Buderus.0 -
kn-10
A KN-10 boile woul be perfect for this application. 1 million Btu 98% condensing with 3 to 1 turndown.
Sweet machine
www.hydrothermkn.com0 -
Another possibility:
The Trinity 400 series from NTI offers a 16:1 turndown ratio. Put in two, stage them with a Tekmar, and you have the load covered from 25kBTU/hr all the way to 800kBTU/hr, for a combined turn-down ratio of 32:1. Can't really get any more efficient than that.
Two little munchkins would do about the same with a range of 80kBTU/hr to about 798KBTU/hr or about 10:1.
With that low of a supply temp, just about any condensing boiler should be in the 98%+ AFUE range, so I'd go with a condensing boiler for sure.
One other thing you might want to mull is the following: Cost of electricity vs. the supply temperature for the heat pumps: At what water temperature is the plant operating at the most efficient (in therms of $ and cents) ratio of electricity to fuel costs.0 -
condensing boilers
look at this web site,gasmaster-ind.com.they make condensing boilers from 200000 to 8000000. the feed water temps can be very low,about 60 degrees. 7year thermal shock,etc.0 -
Thanks
for the input guy's.
You have given me a good jump on the direction to take.
I'll let you know how the meeting goes.
Keith0 -
Most of the loops I deal with use staged hydrotherm boilers, Have always thought a staged setup with a modulating or condensing first and a basic dirt simple staged rack would be the best of all worlds. might want to verify that 95* and check the specs of the heat pumps 70-75* is what we run loops at during the winter. and stage the tower for 95* or so in the summer0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements