Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Does tankless for baseboard on steamer require circulator>
Steve Garson
Member Posts: 191
Close to finishing a new steam boiler installation with a 4-section WM. The small (13,000 BTU heat loss) and 33 feet baseboard) loop will be installed to a 6GPM Everhot vertical tankless connected to the steam boiler.
Will the pipiing between the boiler and tankless require a circulator, or will will convection be adequate?
Will the pipiing between the boiler and tankless require a circulator, or will will convection be adequate?
0
Comments
-
I would install a circulator. System will operate much better.0 -
tankless circulator
Ditto on the circ...just make sure it's a high temp impeller and rated for the temp....a normal circ won't last pumping 212*+ water
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements