    steam pipe insulation

    Is the R-Value of old asbestos pipe covering the same as fiberglass? The asbestos was installed in the late 1920's. Does anyone know the R-value of each?
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    There was an "R-Value" back then, but it was only a step in the equation to get "U-value".

    Corrugated asbestos and magnesia/asbestos both have an internal conductivity value of about 0.5

    R = thickness (inches)/internal conductivity

    R = 1 / 0.5

    = 2.0

    So, the old "snowmen" and piping should have an R-value of about 2.0 per inch.

    Fiberglass batt insulation claims up to about R 3.7 per inch under ideal circumstance.






  • Steamhead
    Steamhead Member Posts: 17,387
    Where

    did you find that? I don't recall seeing it in any of my Dead Men's books.....

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • michael_15
    michael_15 Member Posts: 231
    R Value of Asbestos

    For some reason, I can't find this stated on the web. This might be because nobody measured and/or asbestos came in a few physical forms which had different R values.

    There is some published data about the thermal conductivity of asbestos, however, usually given in W/(m*K). You can convert this into R-value per inch (which is usually in (ft^2*F*h)/BTU) as follows:

    R value = 1/(6.94 * thermal conductivity)

    Where R value and thermal conductivity are in the units described above.

    I don't have my CRC or anything with me so I don't know the thermal conductivity for asbestos. However, if you google for "asbestos" and "thermal conductivity", you'll find a few links that show the thermal conductivity. They disagree, of course.

    http://hyperphysics.phy-astr.gsu.edu/hbase/tables/thrcn.html

    Thermal conductivity of 0.17 (after converting units)

    R value of 0.9/inch.

    http://www.projects.ex.ac.uk/trol/dictunit/notes5.htm

    Thermal conductivtiy of 0.2

    R value of 0.7/inch

    http://www.projects.ex.ac.uk/trol/dictunit/notes5.htm

    Thermal conductivity of 0.16

    R value of 0.9/inch

    http://hypertextbook.com/physics/thermal/conduction/

    Thermal conductivity of 0.05 to 0.15

    R value of 1.0 to 2.9/inch

    http://electron4.phys.utk.edu/141/nov3/November 3.html

    Thermal conductivity of 0.084 (after converting units)

    R value of 1.7/inch

    The interesting result of this exercise (for me) is that the thermal conductivity of asbestos, well, isn't very good. Fiberglass usually has a stated conductivity of 0.04 W/(m*K), which corresponds to an R value of around 3.6/inch. (It would probably be 3.7 if I had more significant digits.)

    Perhaps asbestos also offered good radiant resistance (though looking at it, I can't imagine why) or people just liked it 'cause it was easy to apply and/or because it was fireproof. . .

    -Michael
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    From "Mechanical Equipment of Buildings, Volume I", 1916, Harding and Willard.

    Got it from Dan's book auction a couple years ago. An absolute gold mine of info.

  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    From the Book Mentioned Below

    "The internal resistance of a material is equal to the reciprocal of its so-called internal conductivity (C) multiplied by its thickenss and is represented by the fraction x/C, or 1/Cu, in the case of materials for which the conductivity (or conductance) is given in terms of the construction or thickness stated. For example, the internal resistance of 13 in. of brickwork on the basis of a value of C of 5.0 is 13/5 or 2.6. The internal resistance of 2 in. hollow clay tile based on the value of Cu of 1.14 is 1/1.14 or 0.877."

    From the same text: "U = 1/[the sum of] R1 + R2 + Rc"

    Since modern "R-value" is the reciprocal of U-value, I believe the "R" in that first equation is the same.

    Some common "C-values" for old insulation materials (per inch of thickenss):

    Asbestos sheet, 0.29

    Asbestos board (corrugated), 0.48

    Asbestos wood, 2.70

    Asbestos mill board, 0.843

    Magnesia board, 0.51

    Magnesia (85%) and Asbestos (15%), 0.508

    Celotex, 0.34

    Corkboard (pure) & Regranulated Cork, 0.3 (avg)

    Hair Felts & Hair/Jute blends, 0.26 (avg)

    Insulite, 0.34

    Masonite, 0.33

    Rock Wool, 0.27
  • michael_15
    michael_15 Member Posts: 231
    looks right

    Looks right in terms of your assumption of where the "R"'s are in your equations. The data I have about the other materials here where published data is still available (rock wool, cork, etc.) comports with what you have there, so this would seem to suggest that the C values given are indeed in the right units for direct conversion to R value.

    I guess it just remains to be known whether the stuff they insulated the pipes with was the same R-value. It agrees fairly well (at R=2) with the other stated R-value calculations for asbestos above, which vary from around 0.7 to 2.9/inch.