condensate aux. system

bob young
bob young Member Posts: 2,177
any comments for manufacturer preference of pumps on baseboard loops off steam system? was using taco 007 but last two failed in very short time frame. pumping out of boiler.

Comments

  • tommyoil
    tommyoil Member Posts: 612
    Are you using

    any bypass to temper the water at the circ???
  • bob young
    bob young Member Posts: 2,177
    no bypass

    installed without bypass but i can see i may have to possibly change my thoughts on that.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,054


    You probably need a bypass as the water is to hot for the pump. Also a bronze body pump is best. Get a copy of Dan's book on this site "How Come" It ells you exactly how to pipe and install this

    Ed