Determining loop lengths
JimmyJam
Member Posts: 78
Any suggestions on how to determine loop lengths already installed in slab? I was called out to determine why a 10 year old radiant floor heating system has never kept up in cold weather, I found an office area of approximately 750 sq ft, 75' away from supply and return manifolds to be serviced by (2) 1/2" loops (or so the owner states). The loops are supplied off the same manifold as a 1,700 sq ft. shop area that he has valved off as equipment in this area produces enough heat for this area. (This area we believe is serviced by 5 loops of 1/2" tubing.)Copper fin boiler was installed about 6 years ago and of course trips on limit when office area calls for heat, previous contractor has (2) 26-96 pumps in series which tells me???? So to make a long story even longer, is there any way to determine loop lengths that may have been installed for office area? I will need to replumb manifold system but want to determine whether I can correct office heating problem with installed loops.
Thanks for any help!
Thanks for any help!
0
Comments
-
You are in luck
with compression fittings on the various loops you could disconnect and use a garden hose to fill and purge a loop. Then use an air compressor to blow out the water into a bucket and measure the amount.
Make sure you have a compressor with enough fizz (pressure and cfm) to completly blow out the water.
The water can then be converted into loop length. 1/2" pex (1/2" id) holds .920 gallons per 100 feet of tube.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thanks Hotrod!
This is why I visit this sight so often!!!! Does anyone know what the manufacturer is of this tubing? It looks similar to Rehau but has a deeper reddish color to it and I have not pulled off manifold to see if it is PAP pipe yet.0 -
Looks a lot like
DuraPex. It was also sold under the Heatway or Watts Radiant name for awhile. It was sold as a non barrier plumbing tube, dull finish no EVOH barrier.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
loop lengths
are there any labels, markings on the tube?? the tupe if been installing is labeled every two feet from 2 ft to 600 ft,if your lucky enough to read them you could figure out the loop length. good luck..........mike0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements