Customer has a Weil-Mc sgo gold steamer w/tankless and controlling domestic hot water is a Taco 5000 mounted 7" horizontal from hot outlet from coil, valve unit developed leak at valve stem after approx 2 years,
Aqua stat set @180 and diff. set between 5 & 10 degrees, water level is at 1" below manufactures line on boiler (in bossed on sheet metal) at rest and raises approx
1/4" when running. It seems the valve gets to hot on inlet side. City water, doesn't seem to have any corrosion.
Question is; would you guys heat trap this particular valve like the watts 70A series.
Aqua stat set @180 and diff. set between 5 & 10 degrees, water level is at 1" below manufactures line on boiler (in bossed on sheet metal) at rest and raises approx
1/4" when running. It seems the valve gets to hot on inlet side. City water, doesn't seem to have any corrosion.
Question is; would you guys heat trap this particular valve like the watts 70A series.
0
Comments
-
all tstatic mixers need heat traps, to get them to move ...
at least a little, so they dont get jammed in one position from a mineral deposite produced ridgeline0 -
heat trap....
Could either of you elaborate on the piping arrangement of of your "heat trap" setup, I may know what it is but I don't follow you.
I probably would not place the mixer so close to the boiler jacket just to stay away from the radiant temp and ambient temp which could effect the operation and longevity of the valve.
Best Regards,0 -
simply a ft up/down unisulated legnth of hot supply pipe...
that causes a convective cool down of even when no water is drawn - and thus a slight movement of the themostatic mixing valve
see http://www.wattsreg.com/pdf/1915328.pdf0 -
Taco 5000
I've been using taco mixing valves for about a year or so no promblems but as with any mixing or tempring valve a thermal cooling leg is necessary in my mind and if you research you'll find most coil and boiler and valve manbafactors recomemend it so why isn't it done because besides it taking some time you also have to read the direction which seems not to happen to often in the real world .I would have it repiped with 2 unions and tee's for foture ease of the soon coil cleaning to come peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0 -
Pressure
That is good place to install a relief valve. when the boiler is steaming that coil is seeing about 215°F0 -
A heat trap is not required when using a taco 5000 series mixing valve. It can be installed in any position without any degradation in performance. The thermostatic element ensures the desired mix temperature within the minimum/maximum 85 to 150 degrees range.
Taco, Inc.
Joe Mattiello
Technical Service Technician
joemat@taco-hvac.com
401-942-8000 X 484
www.taco-hvac.comJoe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
thanks for the info - good thing you monitor this site....
i would never have known that - i just though the missing heat trap in the diag was for simplicity or oversight, tell your people to revise the pdf to spell that out
this saves so much trouble - many times there just is no room for a heat trap - expect a pickup in sales!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements