Small heat load for radiant floor
kevin coppinger_4
Member Posts: 2,124
the method of radiant be? Slab,Staple up, etc. I did a job like this two years ago for a friend in his new wood shop. It was slab on grade three circuits, water temp of 120F and heat loss of about 19K I used a LP water heater and it seems to work well (except for the cost of the LP)...I guess the next thought would be is there a conversion to a hydroair system in the cards down the road...if so maybe a boiler would be better in the long run...kpc
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
I am
designing a job for an addition where they want radiant floors. The heat loss $ 10 degrees outside air is 24,000 btuh. The existing heating system is a heat pump and they have electric water heaters. There is a propane tank for their oven that they would like to draw from. What would you guys use for hot water source? WW
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
It will be
half slab over tubing over styrofoam on top of existing slab. The other half will be joist trak plates. I was thinking propane water heater, but the efficiency is low. To go up to a boiler seems too pricey, however an upgrade to an idirect might be good for their domestic hot water. I've heard nothing positive from those who tried to use tankless water heaters. I guess I'm just fishing for options I don't know of. WW
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Wayne
Look into the Buderus GB142. You may have to wait alittle for the L.P. conversion but give them a call.
Scott
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
A tough call
A LP or electric HW tank could meet that load. Not the cheapest way depending on KW cost or a low efficiency LP WH.
The 50,000 Munchkin would be a good choice, if you can upsell them on the higher efficiency. Generate their DHW with it and show them an efficient heat and DHW sourse Fuel prices are climbing as we speak, an ideal time to sell high efficiency equipment
If you go with a LP water heater be sure to run it up around 130° or more and use a small mix valve. Running them at normal slab temperatures really sweats (condensate)them to death quickly!
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thanks Hot Rod
your comments mirror my thoughts exactly. I'll price both ways and let them know the long term ramifications. After that they will know what to expect. WW
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements