how much condensate per therm NG?
for going through the stoichiometry. (sp?) My chemistry was some time ago.
Dale0 -
I don't think so.
I just think that you discovered experimental error. I'd trust the measurement that you are taking at the boiler outlet as correct, especially if you have calibrated the thermometer. The copper tube wall is almost transparent thermally, (less than 1 deg drop).
Dale0 -
Ok lets try expansion its one of the refrigeration cycles
There is quite an increase in area from the combustion to exit. So the stuff cools, the h2o drops out of the mix, and gives up its latent heat, the three inch exit is a lot larger than the 1.5 inch gas valve venturi so you have a net cooling
so perhaps, the are getting cool, outlet temps, and lots of water removal, but maybe they are not recovering quite as much latent heat as they would have you believe but they are definitely doing better than the munchkin or the vidoden on high temp loads
I have to look at Buderuss docs, their new wall mount is aluminum also have to see what it can do
OK
That sounds more plausible....but still skeptical.
Dale0 -
> Try 60 degrees and 55 degrees.
(a) We are now getting several days when the number of ddays is the same as in November. But the Munchkin is consuming 20% more gas. Changing the baseline can't possibly change that result.
(b) The previous (CI) boiler did not show the deteriorating trend, using the same (65F) baseline.0 -
Do Propane
Hello Micheal,
Can you flesh out propane for us in a similar way? Great education, information for all.
Thanks,
Dale0 -
Seems unreasonable though
Don't you think? To what do you attribute the difference in fuel consumption. Is the munchkin running poorly? Do you suggest they all run this way?
I think the difference must be in the experimental technique. (not to diss your efforts at all). It's just that Comparing one installation to another by way of DD seems fraught with potential error. One wants something harder with which to check or correlate the DD data. Like a btu/meter on both boiler outlets.
If it were a Vitodens, I would definitely check the technique before I questioned the boiler.
Dale0 -
propane
Propane is C3H8.
C3H8 + 5O2 -> 3CO2 + 4H2O
Releases 2292 kJ/mol if the water is allowed to condense. Since 1 therm = 105500 kJ, this reaction must happen to the (105500/2292)=47.5 molar equivalent level.
47.5 molar equivalents * 4 H2O per equivalent = 190 moles of water = 3422 grams at 18 grams/mole.
3422 grams = 0.904 gallons.
Goodness, this sounds like what I did all through college.
-Michael0 -
> way?
If I knew, I wouldn't have started this thread.
I have no idea what you mean. I can't compare the gas consumption of an old boiler to that of a new boiler? Isn't that the bottom line?
Sure but,
There are other uncontrolled variables, among them the actual DD experienced at your house and the use and occcupancy of the house. Hard to account for 20% Is the munch driving dhw as well?
Bummer if the new munchkin is not doing as well as your old CI boiler. Have you done the flue gas analysis? Is it running well? Is there something that you suspect in the Munch design that accounts for the difference?
Dale0 -
No.
I didn't say that. It's doing slightly better in moderate weather, no difference in 0F weather (design is -10F, which we didn't reach this year).
Yes, it's just fine.
This is beyond my expertise. But it was doing fine in the fall, maybe 30% better than the CI boiler.
another calculation of interest
If I put condensate per therm (1.1 gals) together with the latent heat of vaporization for water (970 BTU/lb) and the weight of one gallon of water (8.3 lb), I come up with a theoretical saving due to full condensing of 9000 BTU per therm, or 9%.
YMMV; in fact I am currently condensing only half this amount (i.e. about half a gallon per therm), even though my return water never exceeds 120F.
This calculation has also made me realize that any problems with the condensing process can't possibly explain a 20% increase in usage per degree-day. In other words I didn't need to start this thread at all...I will have to look elsewhere for the explanation, as some people have already told me in posts above.0 -
Experimental Error
CERTAINLY accept the possibility.
However, I'm using the supply temp reported by the boiler itself and the flue temp I measure in that port. Guess I could add a bit of slack and put the sensing element an nth away from the HX (instead of 3-4" away), but wouldn't that cause another problem with radiant energy from the HX inflating the air temp?
Guess it's possible that the Vitodens isn't reporting the proper temp, but I try to believe that such an appliance isn't prone to that sort of error.0 -
hard science is soooo soothing to the mind!!! tnx
true - at the end of the day....
Condensing boilers are more efficient, not because of condensing, but rather good combustion and modulation
Gotta Love the Chemists...
..who exercise their learning.0