Hartford Loop

Rob_21
Member Posts: 24
I have a residential steam system with a VERY long hartford loop connection, which I believe is the cause of some major water hammer in the system (see picture).
I realize that I need to have a very short hartford loop, however my question is more about how high that loop should be relative to the default water level. As of right now, it's pretty much AT the level of the water ... should it be lower? Higher? If I decide to have that piping redone, I want to make sure that the height is done properly while I'm in there ...
It seems as though much of the system was installed incorrectly from the get-go, I'm just now understanding things enough to be able to make changes here and there that are helping out (ie, changing wet returns to dry) but this seems to be the last major problem.
Thanks in advance!
I realize that I need to have a very short hartford loop, however my question is more about how high that loop should be relative to the default water level. As of right now, it's pretty much AT the level of the water ... should it be lower? Higher? If I decide to have that piping redone, I want to make sure that the height is done properly while I'm in there ...
It seems as though much of the system was installed incorrectly from the get-go, I'm just now understanding things enough to be able to make changes here and there that are helping out (ie, changing wet returns to dry) but this seems to be the last major problem.
Thanks in advance!
0
Comments
-
A few inches below the water level
Probably two inches. Keep in mind that you may want it about two inches below the running water level, which is lower than the cold water level since when running some of the water is up in the radiators as steam.
-Michael
0 -
correct
if memory serves minimum is 1 1/2 below and that section between your return and loop with the union in it, that should be a close nipple or as short to that as you can get.0 -
Right now the connection is probably about 6-8 inches.
This morning, the hammer was unbelievable and I was finally able to get down to the boiler in time to "catch" where it was happening ... it certainly seemed to be coming right from where the loop lives.
So, I'm now looking at a job that consists of moving the loop down about two inches, and in about 6 inches. Looks like it will also require me to move my new dry returns in a few inches as well. Thank god it's only money ...0 -
While you're at it
If you're going to have someone come in an reipie, you might as well post pictures of the rest of the near-boiler piping to let people here tell you what they think about it.
From the picture, down about two inches wouldn't really push it 2 inches underneath the waterline, but that might just be perspective.
In terms of "in" about 6 inches, just tell them to use a close nipple or what not. As short as possible.
-Michael
-Michael0 -
Will do - I'll post a picture of the system later on.0 -
Rob, you need to check
the instructions that came with the boiler. If you don't have them and the boiler maker is still in business, they should be able to get them to you.
The instructions will have a piping diagram that is supposed to be used when installing the boiler. Among other things, this will show what sizes of pipe are to be used and what their configuration should be- including the Hartford Loop height. Make sure the repiping is done according to the instructions.
The installer should have read and followed the instructions. Sadly, some just use them for knee pads. I think that's what happened on your job.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Yeah, the whole system was pretty much a hack job IMO. The house was previously owned by a couple whose children were electricians, plumbers, and carpenters ... and I'm finding that they cut a LOT of corners in the house.
Case in point - at the water main connection from the street, they used a foot of gas piping to make a connection to the copper used in the rest of the house. I had water pressure problems soon after moving in, and when the plumber took that piece off it looked like rusty Cream of Wheat inside it ... I'm surprised ANY water got through!!
Anyway, I've attached a pic of my boiler and near-boiler piping as promised ... any feedback would be great!
Thanks,
Rob0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 948 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements